question

ecoworld avatar image
ecoworld asked

Intermittent “Low Battery on VE.Bus warnings” from Off Grid Multiplus II

Intermittent “Low Battery on VE.Bus warnings” from Off Grid Multiplus II.

All other devices show normal battery voltages on VRM and all connections are physically good. Any ideas?

Multiplus-II
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solarhack avatar image solarhack commented ·

Hi

A few questions:

  1. What battery is it and have you set the battery settings as per the manufacturers recommendations?
  2. Is the battery sized correctly for the inverters load?
  3. Do you sometimes get DC ripple errors at the same time?
0 Likes 0 ·
1 Answer
ecoworld avatar image
ecoworld answered ·

Guy answered this problem in another post, here is his correct answer:


“Use Remote VE.Configure to download the configuration file from the MultiPlus-II and set the DC input Low Pre-Alarm in the Inverter tab to below 47V Then send it back to the unit.

This will stop the alarm.“

...and it did!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.