Intermittent “Low Battery on VE.Bus warnings” from Off Grid Multiplus II.
All other devices show normal battery voltages on VRM and all connections are physically good. Any ideas?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Intermittent “Low Battery on VE.Bus warnings” from Off Grid Multiplus II.
All other devices show normal battery voltages on VRM and all connections are physically good. Any ideas?
Guy answered this problem in another post, here is his correct answer:
“Use Remote VE.Configure to download the configuration file from the MultiPlus-II and set the DC input Low Pre-Alarm in the Inverter tab to below 47V Then send it back to the unit.
This will stop the alarm.“
...and it did!