question

Albert Mantel avatar image
Albert Mantel asked

Programming relais K1

I have a Multiplus 14/5000/120 (10R-053543). I tried to program relay K1 in such a way that the contact will be closed when AC1 is available. Result: K1 is always closed (zero ohm between NO and COM). Attached the screen of the VEconfigure 3 in the "get settings" mode. N.B. I send the program and reboot the device.

Please what did I wrong. I have browsed the Internet and don't find examples what helps to solve it.



Multiplus-II
capture.png (87.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

You also have to program a assistant to open the relay (when AC IN is not available).

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

offroadflow avatar image offroadflow commented ·

Sorry to open up this topic again.

I'd like to program my MultiPlus 24/3000/70-50 but it's not possible since the software won't let me.

I even switched off the virtual switch, but no difference. What can I do do be able to use K1 + K2 please..?

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ offroadflow commented ·

Can you provide some more information?

What software do you use? Some screenshots maybe?

0 Likes 0 ·
offroadflow avatar image offroadflow Matthias Lange - DE ♦ commented ·

Thank you so much for your reply @Matthias !

I'm using the VE Config 3 on an old WIN8.1 tablet.

Here a couple of screenshots:

16129540708856754643808184697249.jpg

16129541509254137266787149762711.jpg

1612954194701923148452543386440.jpg

0 Likes 0 ·
offroadflow avatar image offroadflow Matthias Lange - DE ♦ commented ·

...and I'm using the MK2 USB interface...

Hope this helps...

0 Likes 0 ·
JohnC avatar image JohnC ♦ offroadflow commented ·

Unless it's been updated before, your firmware is only 152. Not suitable for Assistants..

And you may need to use VEFlash. This should cover your needs, but at least a place to start your research. Heed the warnings too, not for the unwary: https://www.victronenergy.com/live/updating_firmware:updating_ve.bus_products

@offroadflow


0 Likes 0 ·
Show more comments