What would be the advantages and disadvantages of using 2 x MULTIPLUS II 48/5000/70-50 Versus 1 x Quattro 48/10000/140-100/100?
Thanks for your replies!!!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
What would be the advantages and disadvantages of using 2 x MULTIPLUS II 48/5000/70-50 Versus 1 x Quattro 48/10000/140-100/100?
Thanks for your replies!!!
Hi @Muendo. The only real functional difference will be that the Multiplus II has built in anti-islanding, so if you need that you’ll have to add an external anti-islanding device when using the Quattro. The no-load current draw is stated as 60w for a 10K Quattro, and the Multiplus II is said to be 18W so two of them will bring it to 36W. From an installation point of view, it will be more challenging to install the two Multi’s to get them to share the load 50/50 between them.
I had the same question and appreciate the response from @Murray van Graan.
You say : it will be more challenging to install the two Multi’s to get them to share the load 50/50 between them.
Are the loads supposed to be supplied 50/50 , or the first 5K on the 1st Multi, and if 6 or 7K, then the second one provides ? Isn't this the base for the concept of master / Slave inverters ?
Hi @Herve RV Nizard. The loads are supposed to be split 50/50 between inverters. The master is purely the controlling unit, but as far as the load is concerned they need to share that
Hello,
I would appreciate assistance in this as well. I am submitting a proposal today and I'm up against a Quattro vs my 2 x Multiplus 2 on a single phase.
ie: 1 x Quattro 48/10000 vs 2 x Multi 48/5000
If someone could urgently assist be with this i would be eternally grateful
I see the first answer is roughly 10 months ago.
Question 1
Does the Quattro 48/10000 still NOT have anti islanding?
If Not, then to comply with our regulations - how do I deal with the anti islanding
Question 2
Are the Multi's not connected in parallel? OR
Must I split my DB in 2 - One Multi out to one have DB and other Multi to other half DB
As mentioned in the previous post - It seems as if the loads must be split
Question 3
How do I then deal with the batteries - Are they on the same bus as BOTH Multi's and the Battery?
Should one Multi be off or disconnected - that all the battery power then gets distributed to the remaining Multi.
Question 4
I read a while back that the Multis must be from the original "batch" / Firmware. What happens if one has to be replaced? A previous reply was that Victron would then replace both - Is this indeed the case?
I am using two SEPARATE arrays
first array goes to one x MPPT 250/85
second array goes to the second MPPT 250/85
My intention is, is to take each array to a separate combiner box BUT to then take each combiner box to ONE BUS - In this instance probably one to the first multi and the second to the other multi - being that they are connected in parrallel and on the same bus anyway.