question

Abraham Munene avatar image
Abraham Munene asked

Three phase set up - Quattro 48V/5000VA/70A-100/100-S/230V VE. Bus Inverter/Charger plus two MultiPlus 48V/3000VA/35A-50/230V VE.Bus Inverter/Charger

Hi,

Can I use the following connected in a three-phase set up: -

  1. One - Three phase set up - Quattro 48V/5000VA/70A-100/100-S/230V VE. Bus Inverter/Charger plus
  2. Two - MultiPlus 48V/3000VA/35A-50/230V VE.Bus Inverter/Charger

If so how would I go about it?

Assistants
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

"All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number."

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Abraham Munene avatar image
Abraham Munene answered ·

Thank you Matthias. Please share a schematic diagram showing a three-phase setup using the MultiPlus-II 48V/3000VA/35A-32/230V Inverter/Charger.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@ammunene

In the article linked by Matthias Lange. you will find several linked documents with examples of AC and DC.

https://www.victronenergy.com/live/_media/ve.bus:rva_-_theory_on_wiring_large_systems.pdf


0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ Alexandra ♦ commented ·

Hi @Alexandra That article is about parallel systems, not 3 phase systems.

@ammunene

This is a good document:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

0 Likes 0 ·
Show more comments