Parallel config with Multiplus and Phoenix inverters

Hi is it possible to run 1 Multiplus 48/3000/35 and 2 x Phoenix 48/3000 inverters in Parallel? where the Multiplus and a SmartSolar MPPT 250/100 is used to charge the battery bank and the Multiplus and Phoenix inverters supply the peak AC loads.

Thanks,

Jannie

battery chargingPhoenix InverterVEConfigure 3Assistants
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

Howsit.

All VE.Bus devices to be used in a parallel or three phase / split phase configuration need to be on exactly the same firmware.
Multiplus and Phoenix inverters will have different firmware numbers.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phil Gavin avatar image Phil Gavin commented ·

Check that, I found that Phoenix inverters are fitted with Multi chips.

You still need the same chip firmware though.

0 Likes 0 ·
tuky avatar image
tuky answered ·

Tried it. Not working. I got the message that I can not connect Multiplus and Inverter.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
You cannot mix different inverter types. This much is documented.
2 Likes 2 ·