System:
Two Quattros - setup in SplitPhase, ACin1 has a generator, ACin2 has the grid
Four MPPT Solar controllers with a total of 56 panels
Large 1400Ah Lithium Battery managed by Batterie's internal BMS that communicates with Venus via CAN-BUS.
Venus is configure: with ESS, sell to grid,
Problem:
When the BMS send to High Voltage Alarm to the Venus, and the Venus sends me an alarm, but does not seem to be doing anything to stop charging the battery. There are six devices that can charge the battery. (2) Quattros and (4) Smart Solar Charger MPPT, they are all controlled by the Venus. How can I get the Venus to hold on charging until the alarm is off.
If the alarm is present for a long time the Batteries internal BMS will disconnect the battery from the system, I have seen strange voltages of 60V to 66V DC, in the DCbus.
Ideas?