Hello.The datasheet of inverters specify the peak power. How long does this peak last?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello.The datasheet of inverters specify the peak power. How long does this peak last?
Here is some further details courtesy of Victron training presentations from @Margreet Leeftink (Victron Energy Staff) and information from @Johannes Boonstra (Victron Energy Staff) - famous Multiplus Overload webinar.
Thank you Guy, very good and important informations, as always from you...
And as usual, just a messenger passing along something I learned from others :)
Thanks for the information, this is incredibly helpful!
I'm running into a similar problem where I'm not sure if my system is "OK" or not. My battery bank system is paired with the MultiPlus 12/2000/80 inverter/charger, and when I run my air conditioner the system temporarily hops to ~2500W power draw, with the alarm light flashing.
I'm not sure how long the air conditioner will temporarily pull this amount for, but am I reading the above chart correctly that it can pull 130% of nominal power (2000W) for 30 minutes? If so, that should be more than enough time, especially given the sporadic nature of the A/C booting up.
Thanks in advance for the help!
Hi: After reading the above I am still struggling to understand what is meant by maximum apparent feed in power and peak power. If we use the Multiplex II 48/8000/110-100 as an example and it is only attached to a sufficiently dimensioned and charged battery what would be the peak AC output power from the inverter? Is it for example 8000VA x 1.3 or 10400VA for up to 30 minutes? I am guessing the peak power figure of 15000W from the datasheet is achieved when the grid or a genset is attached as 10400VA + 8000VA is approximately 15000W.
I am still confuse about the following:
So it seems to me the 2 pictures contradicts. What did I misunderstand ?
Also should we read on the picture 2 third line "Overload where the output voltage remains UNstable"? (instead of remain stable)
Thank you for clarification about that in order to properly size à 15kVA 3 phases system.
Do you know what was your batterie voltage when the inverter derated ?
From my experience with different sizes of inverters (5, 10 and 15kVA) on the quattro range from both 120 and 230V ranges, I can confidently say and I have tested this several and enough times to say that the quattro range does not reach the peak power being twice the nominal power at all and any load just above the kVA P30 rating overload the inverter instantaneously. I am really interested to see test and real data from Victron proving that these inverters reach peak power.
Therefore, I do not recommend to design any system taking the peak power into account as you will end up with inverters overloaded, trust me.
The quattro range is a great product but to me, without any doubt, this is their weakest point in comparison with their competitors on industrial application.
Dear Jesus,
I found your comment while searching for definition of "peak power" for our 15KVA Quattro. Do you think your experience with the quattros that it cannot handle more than P30 would also apply for very short power peaks (0.3 sec)?
Background: We are defining a system with 50-70% standard load as average (K=0.95). By adding a new planned x-ray device it would be a few times 130% for duration of 0.3s per hour (every time a x-ray picture is taken). I am concerned that this might kill the Victrons over time.
13 People are following this question.