3-phase Quattro in ESS change Li-Ion Voltage to 41V for 30 seconds.

The above scenario occurs when there is a mains failure at council level. When we simulate a mains failure with the breaker, then it does not happen.

7c010a8e32b6

ESSlow battery warning
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nigelfxs avatar image
nigelfxs answered ·

Hi Wehrner

ESS can use different sources for the battery voltage measurement. The CCGX menu Settings -> System Setup -> Battery Monitor shows the possible options.

E.g. on my system I have the following:

It is possible that a different "source" may give a more accurate battery voltage, and therefore not cause the Low-Battery Voltage alarm and shutdown.


1583939050051.png (21.9 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Wehrner@onesolar.co.za


it seems your battery disconnects for some reason, what type / size of batteries do you have installed, and what firmware is the battery on?