question

miroslav-katrencik avatar image
miroslav-katrencik asked

Quattro 48v - charger 70A - transfer 100A - generator charge

need information. quatro 48V 70A charger, 100A bridge- ups - in case of AC1 in power failure it will switch to AC2 in where the generator will power 15kw in three-phase connection. The generator is of a low quality but sufficiently saturated to charge the batteries. AC 2 in would in this case only be used for charging. it must not be switched to the power supply of the appliances otherwise it will damage computers. it is possible?

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
ben avatar image
ben answered ·

I don't believe so, no.

You can set the Quattro to "Charger Only", but there's no automatic way to do that prior to qualifying and connecting AC2 In.

In addition, you didn't say whether you wanted the Quattro to invert power (for the computers) while charging on AC2 In. It definitely cannot do both of those things at the same time.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

miroslav-katrencik avatar image miroslav-katrencik commented ·

1. grid ups

2. not grid - generator charge battery -inverter load

0 Likes 0 ·