jos-sbr asked

3 fase Multiplus II use of virtual switches.

I have built a 3 phase power assist with 3 MultiPlusII 48/5000 / 70-50 and a GX color control.

I want a pre-alarm if the battery voltage falls below a certain threshold.

In the event of overloading the inverters or low batt, I want to switch off a big part of the load.

For that I need 2 independent virtual switches.

Is it possible to use only the Virual switch of the master to detect overload in the other phases? Or do I have to put the three virtual switches in parallel?

I tried to use the CCGX's alarm relay to detect overload and low batt but apparently that doesn't work, there is also little info about it.

Does anyone have an idea about this?

Thanks in advance.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Jos SBR

There are a couple of ways of achieving this:

In the event of overloading the inverters or low batt, I want to switch off a big part of the load.

for this you could use AC-out2 for these loads

The easiest way to do this, is to use the 'generator start/stop' function of the CCGX relay: set this up to switch on 'overload warning' (and any other condition you want, like SOC, low Voltage, etc.)

You'll have to wire the relay to all phases, and set the following assistants to all phases:


Another option is to set assistants on all phases to detect the conditions you want monitored, and let these assistants switch a relay. connect these relays in parallel and let them control an input to switch ac-out2


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jos-sbr avatar image
jos-sbr answered ·

Ok thanks for your reply!

It works fine with the generater start / stop function in the CCGX !

I had not thought of this.

Strange that the generator start / stop function in the CCGX works and the alarm function does not.

Problem solved !

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @Jos SBR

could it be that you want the 'warning' function and not the 'alarm' function?

0 Likes 0 ·