Kirloskar Generator not connecting

I have a 5KVA KOEL genset which is connected to a 5KVA multiplus 2 inverter/charger for a 15 kWh lithium battery bank. When I tried to start the generator & load the inverter, it is not connecting as I expected. From the sound of the generator,I found it is overloading a bit & relay in the inverter/charger gets disconnected.

So what can be done to solve this issue.

Any thoughts?

battery chargingGenerator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @alby868

Your Multi is certainly capable of overloading your genny, and so likely are your batts. You'll need to set a current limit within the Multi, and you can tune that to where your genny is 'comfortable'

In case the genny is actually being rejected, see here: https://www.victronenergy.com/live/multiplus_faq

The pages of the VE.Config in that article may show the current limit setting too. Hoping you have the kit to do this..

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alby868 avatar image
alby868 answered ·

We have tried the current limiting also but still the relay gets disconnected in Multiplus 2. Is there any option to provide delay manually to relay inside the inverter/charger

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image JohnC ♦ commented ·

Might be possible with an 'Assistant' installed in the Multi, but outta my field. Maybe someone else can help there..

For a 'soft start' you could try enabling 'Dynamic current limiter'.

Some people confuse batt A with ac A when setting input limit, just a possibility.

Sometimes also helps to ensure it's not the genny baulking, these things can happen fast. A monitor light direct off the genny could show that.

Else it's back to that link I posted. I need to tick 'Weak ac input' on my own system for it to accept my genny. So you wouldn't be alone..