Hello
I have installed Quattro 8kva with 8kW Fronius AC coupled with a CCGX 800Ah of batteries. It is an off grid installation with PV inverter assistant on. When I switch on my generator and the Quattro synchronises with it the Fronius inverter disconnects and says error code 107 which meant no grid.
My generator is 4.5kVa but the wave form is poor so I have limited the current to 13amps and I have used the Weak Ac function
From what I have read about the off grid systems in victron literatureI thought that the Quattro would control wave form so the Fronius and Generator could both power the loads and charge the generator.
But from reading other posts it seems the Quattro is just passing the generator AC frequency through and it’s too messy for the fronius to sync.
Is there a way to allow my generator and fronius to work?