Greetings, new to Victron, lots of questions. I have a house bank on my boat consisting of 6 Trojan L16E-AC 6 volt batteries, 3 pairs of 12 volt = about 1100, 20 hour, 12 volt Amp hours. I have two Multi-plus's in parallel (12/3000/120), a CCGX and a BMV712. Everything is working but not sure if everything is optimally configured. I am wondering what the best Charging parameters would be in the VE-config settings. Trojan recommends 14.8 absorption and a 13.5 Float. I’m not sure if these are considered “Traction” batteries as far as the VE-config options for battery types go.
Very recently installed and yesterday powered up the Multipluses from my generator, BMV712 indicated I was down 200 Amps but Charger went into Float right away and continued to do that even when I turned off AC input feed and turned it back on. So I’m thinking that My configuration is incorrect for charging parameters. I tested all cells for specific Gravity and all is well. I’m also wondering what the best method for equalizing these batteries, Trojan suggests equalizing at 16.2 volts for 2-3 hours.
Also, My BMV712 and CCGX both consistently show a voltage .2 volts less than what I read at the batteries.
One more question. If one of the units fails, and I want to switch to a single unit, re-wiring appropriately, is there a way to bring the units back to factory defaults and program with dip switches or do I have to go into VE-config with my windows laptop?
Thanks