Is it possible to configure a low voltage 3-ph off grid system using the Quattros? That is a 230V 3-ph IT network like in Norway.
Thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi @Stevo07
This is not possible without a transformer to convert to a 400VAC three phase supply.
Hi @Daniël Boekel (Victron Energy Staff)
There is no incoming supply however the client has some 230V 3-ph loads, so do we just set up the Quattro as a 3-ph 400V and use the transformer on the output?
Hi @Stevo07
Ah yes that would work, but also take a look at what those loads are, maybe they can be rewired to 400 VAC (lot's of motors and other products can be rewired)
if the loads are motors, maybe a vfd (Variable Frequency Drive) can be used to provide correct voltage / frequency.