Hello.
Is it possible to configure a low voltage 3-ph off grid system using the Quattros? That is a 230V 3-ph IT network like in Norway.
Thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi @Stevo07
This is not possible without a transformer to convert to a 400VAC three phase supply.
Hi @Daniël Boekel (Victron Energy Staff)
There is no incoming supply however the client has some 230V 3-ph loads, so do we just set up the Quattro as a 3-ph 400V and use the transformer on the output?