AC unit and another appliance requires 230 (US). But other appliances need 115v. The mains power going to the device will have to be 115V.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
AC unit and another appliance requires 230 (US). But other appliances need 115v. The mains power going to the device will have to be 115V.
Hello, you would need 2 or 3 Multiplus units to make split fase or 3 fase system. Each Multi must be a 120 V model. Then you have 115 between fase and zero and 220 Between the fases.
best regards,
rob
It's not possible to use 230V for both 230 and 115? Is the 230 dual phase like standard US 230? Can the 230v be stepped down to 115 with a step down unit of some kind. Just trying to find cheapest option.
Use an autotransformer.
https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf