easyplus compact issues

Hi All

I have just fitted a victron system in my latest van conversion and it causing me a few headaches.


Any help is very much appreciated first let me give you the low down on what i have fitted.


Easyplus compact 12v 1600 inv charger

lithium 160 ah smart battery

V E bus BMS

12 65 battery protect

cyrix li charge

smart mttp

712 battery monitor

ccgx colour control

all components are at the latest firmware.

The issue is when running from the battery with the inverter and say im using a coffee machine rated at 1300 watts the dc cuts out a few seconds after the coffee machine is switched on then the ac cuts out. The dc switches back on a few seconds later.

I am presuming this is the battery protect kicking in and out the question is why is it doing this ?

I am new to installing a more advanced system and still learning .


Cheers in advance

inverter current drawEasyPlus
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

miya avatar image miya commented ·

Hi - I am doing a similar install. Can I check - it is this product you have ? https://www.victronenergy.com/inverters-chargers/easyplus-12v-1600va

Thanks.

0 Likes 0 ·
2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @apevan

Please don't use a battery protect between the battery and inverter!! these devices are:

-one way only, reverse current can damage it

Also: inverters have capacitors that need to be charged, this can look like a short-circuit and overload the device.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

apevan avatar image
apevan answered ·

Hi

Thanks for getting in touch the battery protect is fitted between the battery and the dc loads to cut the loads if the battery is run down not the inverter. This is why I can't get my head round the problem I am having.




2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ahhh now it makes sense to me: your battery is not able to provide the current, so it drops in voltage, making both the inverter shut down and the BP shut off the loads.

Also: a 1300W coffee maker usually needs a much bigger inverter, as they tend to be a 'difficult' load with big peaks. (But this one might be no problem, not all coffee machines are alike)

Is the battery fully charged? measure DC voltages at the battery when this happens to know what is going on.

0 Likes 0 ·