cookiedude avatar image
cookiedude asked
Why does it look like i have a low charge limit
I have a fairly simple system Of an MP2 (10000kva) with 4 x pylontech US5000. Where the whole house feed first goes through the AC IN, then it goes from the AC OUT to the consumer unit.
Currently I have wired the batteries through 2 cables (one at top of stack and one at the bottom to create a round circuit) with a 125A DC (48V) fuse on each to protect each cable. So I should be safe to charge/discharge up to 250A (although I think the victron can only charge up to 140A).
My problem is that when using the ESS to do a scheduled charge it seems to limit the charge rate to ~70A (48v)
In VE Configure 3 The Charger tab has a 'Charge current' set to 140A
Anyone know if there is a setting I can change to get a faster charge?
(sorry cant seem to add images to this forum)
ess settings
Yip, site is broken. You can also post at the new forum. Link available in modifications section.
nickdb avatar image
nickdb answered ·
What CCL is the battery sending?
What loads were running at the same time?
What is the temperature?
Any limits in DVCC?
Any input current limits?
4 comments
cookiedude avatar image cookiedude commented ·
CCL is 320A
loads are 0 (I have a solar inverter on the load circuit)
temp is 22 degrees C
There wasnt a limit on the DVCC, but I tried setting one to 200A (no effect that I could see)
There is a 50A (240V) input current limit but I am no where near that (it is currently plling 14A from grid)
Ps. Thanks for the very quick response!
nickdb avatar image nickdb ♦♦ cookiedude commented ·
We’d need to see some charts, so maybe repost at the new site. I covered the generic causes. Did you run through the setup guide for pylon to confirm settings are correct?
Show more comments