I plan an ESS system with possibility for Island Mode. I have AC coupled 22kW PV with 2 Fronius inverters 10 and 12kW. Usually the Peak perfromance is approx 17-18kW. Now I want to add a 3-Phase ESS system and the Factor 1 Rule dicteates at least 3 Multi 48/8000 eq. 24kW. However, the the battery system with 3 towers at 3 Pytes V5A provides me a charge and disccharge Current of 300 A per tower eq. Total 900A. The Multis only deliver 110 A max each for Charge and disccharge current.
So far all good. The question is, in case in Winterseason I have emptied the batteries during night and morning hours and arround midday I would have 1-2 h of Sun, the Limitation of charging the batteries would be in this case the Multis. corrct?
So woul dit be worth installing the 48/10000 instead and raise the max current to 140A each (total 450A so that what ever my PV is capable of, the Multils can back into the batteries?
Any input is appreciated and if this is a increadibly stupid question please let me know and explain what I might have missed... :-)