3Phase MultiplusII 48/8000 or 48/10000 on 9 Pytes V5Alpha batteries.

I plan an ESS system with possibility for Island Mode. I have AC coupled 22kW PV with 2 Fronius inverters 10 and 12kW. Usually the Peak perfromance is approx 17-18kW. Now I want to add a 3-Phase ESS system and the Factor 1 Rule dicteates at least 3 Multi 48/8000 eq. 24kW. However, the the battery system with 3 towers at 3 Pytes V5A provides me a charge and disccharge Current of 300 A per tower eq. Total 900A. The Multis only deliver 110 A max each for Charge and disccharge current.

So far all good. The question is, in case in Winterseason I have emptied the batteries during night and morning hours and arround midday I would have 1-2 h of Sun, the Limitation of charging the batteries would be in this case the Multis. corrct?

So woul dit be worth installing the 48/10000 instead and raise the max current to 140A each (total 450A so that what ever my PV is capable of, the Multils can back into the batteries?


Any input is appreciated and if this is a increadibly stupid question please let me know and explain what I might have missed... :-)

 
               
Multiplus-IIbattery capacity
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@teubeli

I can't answer from a cost perspective but switching some PV to DC based mppts is the best option. Then there is less conversion as it goes straight to the battery bank and you are not limited in any other way unless you have a poor DC wiring set up.

AC charging hard will cause inverter and inverter/charger derating because of heat. (Unless you have air conditioned the room or have amazing ambient temperature.) So even if you uprate the inverter you still are not likely to see the full 140A per phase.

On a side note if inverter derating for load reasons is a consideration them maybe get the bigger inverters. But still get DC based mppts anyway it is always a good combo for moving off grid anyway....

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

teubeli avatar image teubeli commented ·
Hi Alexandra. Thanks for the answer. The PV is a high voltage system and already in place for some years, so chaning that setup is not part of the plan. Also when it comes to optimize the own consumption (use when and what's there) I think the high Voltage PV systems directly into AC is the most efficient way. My plan is not moving off grid but in an outage being able to sustain for some hours/days in max.
0 Likes 0 ·