Hello fellow Victron fans.
I am sure this was discussed before but need some clarifications what is in fact expected. Here we have a customer that has feed-in turned off until the grid meter is changed into a dual-way one. However, each day we see huge ammount of energy fed to the grid which now the customer has to pay for.
Settings:
Last 5 days stats (notice To Grid):
Any suggestions?
Multiplus-IIESSess settings
nickdb avatar image
nickdb answered ·
Hi. You will need to provide a lot more detail about this system and how it is configured.
szdan avatar image szdan commented ·
It's a three phased MultiPlus II setup with one 250/100 and one 250/60 MPPT plus two Pytes E-Box 5kw batteries.
Duivert NL avatar image
Duivert NL answered ·
What do you use as a grid meter?
Also in ESS feed in will never be 0, it will always try to balance loads on grid
7 comments
There is no grid meter. The whole house is on AC Out.
Ok, but it seems way too much for just balancing. Customer has 60kw in a couple of days added to bill already. The two-way grid provider meter is about two weeks away from being installed. But it is worrying meantime.
The customer never hit DOD so never in fact had to touch the grid. However, the Multi's either pull or push through the meter constantly, ranking up cost needlessly. This back and forward is metered.
Duivert NL avatar image Duivert NL szdan commented ·
Ac out 1 or 2?
As nickdb already said, you have to provide all info on the system and settings …
szdan avatar image szdan Duivert NL commented ·
Everything is on AC 1 OUT. Nothing connected to AC 2 OUT. System is pretty striaght forward.
3 X MultiPlus II 5kVA
Cerbo
2 X MPPTs
Pytes BMS
All components on latest firmware. Multis are v510, Cerbo v3.4, etc.
What other details are you looking for?
ejrossouw avatar image ejrossouw szdan commented ·
Have you tried multi phase regulation set to per phase?
szdan avatar image szdan ejrossouw commented ·
Ok, will try for a day. I understand this comes with huge loses though.
Settings look ok to me, did you try a higher grid setpoint? Standard is 50W
External grid meter (em540) is always more accurate then the inverter meter
Have tried with default also, same behaviour. Reason I put it to 20w is to try reduce it. So ideally a meter should be used with ESS systems and not rely on Multi's metering?
dennibu avatar image
dennibu answered ·
Der Mehreigentümerzähler ist nicht ausgeglichen, es ist derselbe wie beim et340. Daher stimmt die Auswertung im VRM nicht wirklich. Man sieht, dass die Deckung in etwa der Einspeisung entspricht. Bei einem Nettozähler wäre das wieder etwa 0.
nickdb avatar image
nickdb answered ·
You have a 3-phase system, it is also set to "total of all phases" for regulation, so it will backfeed to try keep the net usage zero, which seems to be the case on yours.
If your phases are not balanced, it is going to send power back.
Try change the ESS regulation to individual phase, and see if that changes the behaviour.
Try that for about two hours since the post above. Customer called to say that L1 inverter has gone crazy loud and hot which he could see consumption on L2. I guess it was trying to help it out?
nickdb avatar image nickdb ♦♦ szdan commented ·