Grid Feed-In while setting for feed-in is set to OFF

Hello fellow Victron fans.

I am sure this was discussed before but need some clarifications what is in fact expected. Here we have a customer that has feed-in turned off until the grid meter is changed into a dual-way one. However, each day we see huge ammount of energy fed to the grid which now the customer has to pay for.

Settings:

1722605629574.png


1722605748491.png


Last 5 days stats (notice To Grid):

1722606844592.png

1722606857547.png


1722606871078.png


1722606886613.png


1722606903923.png
Any suggestions?

Multiplus-IIESSess settings
1722605629574.png (22.8 KiB)
1722605748491.png (17.4 KiB)
1722606844592.png (48.3 KiB)
1722606857547.png (49.6 KiB)
1722606871078.png (53.4 KiB)
1722606886613.png (53.2 KiB)
1722606903923.png (52.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
nickdb avatar image
nickdb answered ·

Hi. You will need to provide a lot more detail about this system and how it is configured.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

szdan avatar image szdan commented ·

It's a three phased MultiPlus II setup with one 250/100 and one 250/60 MPPT plus two Pytes E-Box 5kw batteries.

0 Likes 0 ·
Duivert NL avatar image
Duivert NL answered ·

What do you use as a grid meter?

Also in ESS feed in will never be 0, it will always try to balance loads on grid

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

szdan avatar image szdan commented ·

There is no grid meter. The whole house is on AC Out.


Ok, but it seems way too much for just balancing. Customer has 60kw in a couple of days added to bill already. The two-way grid provider meter is about two weeks away from being installed. But it is worrying meantime.

The customer never hit DOD so never in fact had to touch the grid. However, the Multi's either pull or push through the meter constantly, ranking up cost needlessly. This back and forward is metered.

0 Likes 0 ·
Duivert NL avatar image Duivert NL szdan commented ·

Ac out 1 or 2?

As nickdb already said, you have to provide all info on the system and settings …

0 Likes 0 ·
szdan avatar image szdan Duivert NL commented ·

Everything is on AC 1 OUT. Nothing connected to AC 2 OUT. System is pretty striaght forward.


3 X MultiPlus II 5kVA

Cerbo

2 X MPPTs

Pytes BMS


All components on latest firmware. Multis are v510, Cerbo v3.4, etc.

What other details are you looking for?




1000066767.jpg1000066769.jpg1000066771.jpg1000066765.jpg

0 Likes 0 ·
1000066765.jpg (205.4 KiB)
1000066767.jpg (215.7 KiB)
1000066769.jpg (195.6 KiB)
1000066771.jpg (210.3 KiB)
ejrossouw avatar image ejrossouw szdan commented ·

Have you tried multi phase regulation set to per phase?

0 Likes 0 ·
szdan avatar image szdan ejrossouw commented ·

Ok, will try for a day. I understand this comes with huge loses though.

0 Likes 0 ·
Duivert NL avatar image Duivert NL szdan commented ·

Settings look ok to me, did you try a higher grid setpoint? Standard is 50W

External grid meter (em540) is always more accurate then the inverter meter

0 Likes 0 ·
szdan avatar image szdan Duivert NL commented ·

Have tried with default also, same behaviour. Reason I put it to 20w is to try reduce it. So ideally a meter should be used with ESS systems and not rely on Multi's metering?

0 Likes 0 ·
dennibu avatar image
dennibu answered ·

Der Mehreigentümerzähler ist nicht ausgeglichen, es ist derselbe wie beim et340. Daher stimmt die Auswertung im VRM nicht wirklich. Man sieht, dass die Deckung in etwa der Einspeisung entspricht. Bei einem Nettozähler wäre das wieder etwa 0.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

You have a 3-phase system, it is also set to "total of all phases" for regulation, so it will backfeed to try keep the net usage zero, which seems to be the case on yours.

If your phases are not balanced, it is going to send power back.

Try change the ESS regulation to individual phase, and see if that changes the behaviour.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

szdan avatar image szdan commented ·

Try that for about two hours since the post above. Customer called to say that L1 inverter has gone crazy loud and hot which he could see consumption on L2. I guess it was trying to help it out?

0 Likes 0 ·
Show more comments