Hi,
im am installing a victron multiplus II with ESS (Austria grid). The ESS is shown to be in off state
Multiplus does not who any lights in remote console.
How can i get ESS running?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
im am installing a victron multiplus II with ESS (Austria grid). The ESS is shown to be in off state
Multiplus does not who any lights in remote console.
How can i get ESS running?
What firmware is on your GX and inverter?
Do you see that your inverter is off?
ESS only works when the switch is in the on position. Or if switched off in software needs to be switched back on.
Switch is in Position 1.
In the inverter die charge led is on, inverter led is off
When 1 disconnect main 230V supply, ac loads an AC-Out get power from the battery. The inverter is than working as expected. But not when using ESS.
The real problem is probably not ESS but passthru mode. On startup the inverter led is on. After exactly 1 Minute Charge led goes on and inverter off.
I set back the multiplus (startet with default settings in VEConfigure and sent the setting)-> no change. Afterward set back venusos with https://www.victronenergy.com/media/pg/Venus_GX/en/reset-to-factory-defaults-and-venus-os-reinstall.html -> no change.
I now tested:
- https://www.victronenergy.com/media/pg/Energy_Storage_System/en/faq.html#UUID-169dbd85-4b6f-814b-33c2-9fa77a6973d2_section-idm4628123204859232885885561444
Q4.1 : ESS → Control without grid-meter setting -> did not change anything
Q4.2: Systems with a canbus-connected lithium system: I have no communication with bms.
Q4.3: When charging the battery is not allowed -> charging is allowed
Q4.4: When discharge is not allowed -and- loads on AC-Out force the Multi/Quattro to exceed the AC input current limit. -> is allowed. Battery voltage is higher than absobtion.
Q4.5 A grid code is in use that requires the enabling of battery discharging by aux-inputs. -> Austria Grid Code default uses AUX input. I disabled AUX input for testing -> no change
Q4.6: LOM: disabled for testing -> no change
So no solution found. Currently I have no idea what else I should test.
My ideas:
- I have no pv inverter configured, solaredge is not supported yet. I don't think this could lead to any problems.
- as inverter ist starting when AC-In fuse switched off I think inverter is working correct.
I think I now read all threads about passthru but did not find a solution.
Is it possible that someone from the support team can help? Are same dbus values of interesst?
I wrote a short script to test mode 3. https://github.com/schenlap/victron_ess3_test
Result is the same, no feed-in. Interessting is that register /Hub4/L1/AcPowerSetpoint does not get reset after 1 Minute. Strange...
18:25:36 INFO test_ess3:75 Verbindung zu 10.0.0.202:502 hergestellt. 18:25:36 INFO test_ess3:45 Aktueller Wert von Register ESS MODE 2902: 3.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register MAX DISCHARGE POWER 2704: 400.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register MAX FEEDIN POWER 2706: 500.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register SWITCH POSITION 33: 3.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register AC POWER 37: 30.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register DISABLE CHARGE FLAG 38: 0.0 18:25:36 INFO test_ess3:45 Aktueller Wert von Register DISABLE FEEDINFLAG 39: 0.0 18:25:36 INFO test_ess3:57 Register AC POWER 37 erfolgreich auf 50 gesetzt 18:25:37 INFO test_ess3:45 Aktueller Wert von Register AC POWER 37: 50.0 18:25:37 INFO test_ess3:85 Waiting 65 seconds to reset register 18:26:42 INFO test_ess3:45 Aktueller Wert von Register AC POWER 37: 50
I did a FW update on my MPII last week and the raspberry pi that controls it. On boot, it went into passthrough. I thought maybe config had gone, so I tried to reload ESS via VRM. It was then that I realised that my pi had not connected to the Internet. Once I'd fixed that and I could see the installation in VRM it changed to bulk. I didn't need to reload any config.
I run ESS with the MP charging the battery, no PV configured and an external CT. Grid is set to France. Your description of startup matches mine. At some point, early on I think, there is a loud rattle as the relays do a test. Are you showing ESS relay test completed under advanced
50 People are following this question.