Random 3x Multi Plus II 30 sec restart

Hi, My three phase system + cerbogx + Shunt + Daly BMS started to restart in last 6 months. Maybe 30 occurences. System shuts down and reinitializes after 30 sec. Battery random, but not flat 30-99%. BMS driving only LIfepo batteries, no direct shutdown or charge control. Looking for a way how to find a reason, why the devices goes to reboot. There is no info available in GX, not home assistant over modbus. I am not sure what log files on cerbo should have relevant info. Thanks

Multiplus-IIcerbo gxreboot
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
hipik634 avatar image
hipik634 answered ·

thanks for the ideas ... i updated it to current SW versions while I was in the mood. So faulty contact was probably the cause. It randomly lost contact switching the inverters off in combination with normally closed AUX2. Cheers

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

30 second intervals are the default restart interval after overloads, relay test failures etc.

It will attempt this 3 times before stopping.

Your GX/VRM should log the cause under notifications/alarms, or even the VEBUS status widget.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hipik634 avatar image
hipik634 answered ·

Today the reset was at 2:20 (the one that has awaken me), so I would expect it is shown on this graph. It came off 4 times this night. Can I find the reason, that if went off? In my setup I have set up an emergency button to disable inverters. Do you think it might work the same way - like if the contact would be loose. But if I press that one, the system shuts off but an alarm is correctly shown in events.

1722341142240.png

1722340772878.png


1722340772878.png (15.2 KiB)
1722341142240.png (112.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hipik634 avatar image
hipik634 answered ·

this tells me, that the relay input shut it down, right?

1722341635767.png


1722341635767.png (87.2 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·

Open the alarms and warnings vebus widget, see what it reports.

I can see your system is switching to invert, so possibly grid rejection or failure, and it goes off soon after.

Most common reason for this is either an overload, or, the surge on the battery at changeover is knocking the BMS over which will affect stability.

Not an easy one to diagnose via the internet.


1 Like 1 ·
hipik634 avatar image hipik634 nickdb ♦♦ commented ·

nothing in alarms .... the loads are supposed to be low overnight.


1722344656495.png


1722344798004.png

0 Likes 0 ·
1722344656495.png (115.2 KiB)
1722344798004.png (79.3 KiB)
nickdb avatar image nickdb ♦♦ hipik634 commented ·

Chances are it is then battery related, as a result of the system cutting over to invert.

An example of this is a brown out, where grid loss is not "clean", and it can, despite low loads, cause issues for a BMS, more commonly seen on smaller battery packs or sensitive/misconfigured BMS's.

You have not detailed your battery, though with the DALY (unfortunately unsupported), I am presuming it is a DIY battery - where these sorts of problems are not uncommon.


Something else to check. How have you configured the inverter cut-off voltages/soc (via veconfigure) and, the ESS assistant dynamic cutoffs?

Another consideration, is that a 3-phase system by default switches as a group, so if one inverter has an issue, they will all switch. With vequickconfigure you can set them to not switch as a group (requires redoing your config), which may show if one unit is having a problem or if all are.

If you use a mk3 you can go to the grid tab and open the NS protection log. It should record what the reason was for the loss/rejection of grid.

1 Like 1 ·
hipik634 avatar image
hipik634 answered ·

ok, i will try to pinpoint it later today. The battery is DIY, but monitoring shows no unusual stuff . BMS is standalone,it is just configured to limit possible margin states. The true values comes from the shunt. But you can see there was no spikes by that time. I have put Home Assistant and switches on an UPS to get the data during shutdown. Maybe the disable feedin signal has something to it. I have a dedicated wiring telling the inverters to cut of the grid if the distributor chooses to (HRN-34 relay, controlling phase and voltages and flipping relay if not ok) . Maybe it is something to check. I can see from the previous images, that the relay changed state.. I use these two assistants below:

1722349109213.png

1722349336115.png

1722349356787.png


1722348817223.png



1722348817223.png (95.3 KiB)
1722349109213.png (13.9 KiB)
1722349336115.png (18.5 KiB)
1722349356787.png (14.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hipik634 avatar image
hipik634 answered ·

So after some fiddling with the emergency switch i have been able to shut down the inverters. So I changed the closed/open on AUX2 behavior, from NC to NO. I will leave it for few days, if it holds ...

1722357312382.png


1722357312382.png (8.3 KiB)
2 |3000