Multiplus II 3 Phase - Different PN

Hello,

i installed on MP II 5000-48 3 month ago in a single phase setup up. Now i order 2 new units to expand to a 3 phase system. The product numbers has changed:

1 x PMP482505010

2 x PMP482505012

Would they work together?

Regards Matthias

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Justin Cook avatar image
Justin Cook answered ·

That particular difference in PN only indicates that the units are from different factories, but the units should be identical internally and should give you no issues in compatibility. Make sure you have them all on the same FW prior to commissioning though.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

steel avatar image
steel answered ·

Thanks, i askes because the lower cover has chaneged an uses now different screws