Hello,
i installed on MP II 5000-48 3 month ago in a single phase setup up. Now i order 2 new units to expand to a 3 phase system. The product numbers has changed:
1 x PMP482505010
2 x PMP482505012
Would they work together?
Regards Matthias
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
i installed on MP II 5000-48 3 month ago in a single phase setup up. Now i order 2 new units to expand to a 3 phase system. The product numbers has changed:
1 x PMP482505010
2 x PMP482505012
Would they work together?
Regards Matthias
That particular difference in PN only indicates that the units are from different factories, but the units should be identical internally and should give you no issues in compatibility. Make sure you have them all on the same FW prior to commissioning though.