VE.Bus DC Voltage suddenly fluctuating even without load.

Had system installed for 9mths running perfectly but all of a sudden VE.Bus voltage is unstable, even under no load. I currently have it "charger-only" because I get constant alarms and shutdowns if inverter operates.

I've read other posts about this which talk about DC ripple and I plan to check all the connections, but what is weird is that there have been no issues for 9mths whatsoever and that this is occuring under no load.

I did a firmware update yesterday, which involved restarting everything and reapplying configuration and interestingly this did resolve the issue for a while. But later the same day, after a 25min DESS discharge at 210A, it reoccured.

Any thoughts or idea?

1720346846665.png

Multiplus-II
1720346846665.png (130.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
daniel-feist avatar image
daniel-feist answered ·

This was bad connection in the end. Not sure exactly if it was crimp, loose bolt of battery switch issue but I replaced battery switch, got electriciation to recrimp this connection and check all nuts with torque wrench and I'm back in action..


1722004227999.png


1722004227999.png (1.7 MiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image Justin Cook ♦♦ commented ·

What brand and model battery switch is that? You appear to be running a 48vNom system and there aren't many (if truly any) rotary-style battery switches that are rated to be able to handle 60vDC.

0 Likes 0 ·
daniel-feist avatar image daniel-feist Justin Cook ♦♦ commented ·

It's the Victron one. Apparently rated for 60v.

0 Likes 0 ·
Show more comments
nickdb avatar image
nickdb answered ·

Connections can fail over time due to constant cycling. I have found poor connections many months after they were originally made as the failure eventually cascades into a real problem, but prior to that it all appeared fine.

Start with the basics.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daniel-feist avatar image daniel-feist commented ·
Will do. Given the low voltage alarm was only showing on L1, does this imply that there is an issue between busbar and L1 Multiplus? Or does the low voltage alarm on L1 represent the shared VE.bus voltage somehow and the issue could be anywhere?
0 Likes 0 ·
nickdb avatar image nickdb ♦♦ daniel-feist commented ·
Is your system 3-phase?

If this fluctuation is unique to one phase, then it is a safe assumption that the issue is localised there.

0 Likes 0 ·
daniel-feist avatar image daniel-feist nickdb ♦♦ commented ·

Yes, 3-phase. The low-voltage alarm is overwhelming occuring on L1 according to the advanced page, however the VE.Bus DC voltage fluctuations (pasted above) as well as the DC ripple alarms (bottom below) are not phase-specific. My assumption based on this is focus on busbus->L1 inverter first, then reaccess.

1720368657083.png

0 Likes 0 ·
1720368657083.png (66.1 KiB)