question

maartenkg avatar image
maartenkg asked

Victron-Pylontech US5000 ESS (dis)charge limit?

Hi everyone, we recently installed an ESS consisting of 18x Pylontech US5000 and 3x Victron Multiplus-II 48V/10000VA/140A-100/100/230. We would expect a maximum (dis)charge of around 3x 8.000W (combined 24.000W), but when checking the VRM app and setting it the maximum 8.000W per inverter, per phase it just doesn't go above a combined 15.000W. I've been checking all sorts of settings, but cannot find where there could possible be a limit in place. Can anyone help me out? P.s. at the same site we also installed a 12x Pylontech US3000 combined with 3x Victron Multiplus-II 48V/5000/70-50 230V and they perfectly do the max of around 4.000W per inverter.

Multiplus-IIbattery chargingPylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@maartenkg

Sounds like the system does not know all modules are there.

Check under the pylontec see the CCL and DCL or use vrm advanced with the widget there.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

maartenkg avatar image maartenkg commented ·

Thanks, in VRM advanced I see CCL 960A and DCL 960A. Should be enough. How can I see if all 18 modules are known to the system?

0 Likes 0 ·
Show more comments
maartenkg avatar image maartenkg commented ·

Thanks so much for the feedback, ok the 960A seems then not enough. I do not have the "Details" Tag though. Any other place where the 960A can be increased?

0 Likes 0 ·
maartenkg avatar image maartenkg commented ·

Aaah I misread, 960A IS enough.

0 Likes 0 ·
Show more comments
maartenkg avatar image
maartenkg answered ·

Thanks all for the input, is there in VRM portal any option to add modules and/or increase the max AC current that can be drawn by the Victron's? We think that we maybe have put in a limit when installing the Victrons. Are these settings only configurable at location and connecting a USB dongle to the Victrons?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Google remote veconfigure.
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ nickdb ♦♦ commented ·
Ac input current liit can be set on the GX and in the vrm side bar if you enable inverter controls.
0 Likes 0 ·