Mains on does not come on when on AC2

Quattro 5000, has been installed and running perfect for 3 years.

Suddenly AC2 stops working, shows no "Mains On", Have correct voltage in 230V AC

Tried interchange cables from AC1 and AC2, same problem remains, so there's something wrong on the input channel AC2, any ideas on what might have happened or how to do more fault finding ?

voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

So to be clear

1. on AC1 in you have mains/Grid power

2. on AC2 in you have a Generator supplying backup power


If you now put

1. on AC1 you connect the Generator

2 On AC2 you connect the Mains/Grid power


and then the generator now works ok on AC1 but the mains power or Grid Power does not connect on AC2 when the generator is off

If thats the case then maybe the AC2 connection relay has failed and you would need to take the unit in for checking.




2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sydfart avatar image sydfart commented ·

Thanks exactly, so probably next would be to have the relay checked, I then assume there's no fuse or more simple explanation to the failure