Hello,
we have the following Victron setup and unfortunately a problem with the EVCS. "Waiting for Sun"
3x Victron MPPT450/200 => 30kWp solar panels
1x Fronius Symo Advanced 20.3 => 18kWp solar panels
3x Victron MultiPlus 48/10000 => 3 phase ESS, Fronius zero feed-in
20x Pylontech US3000C @Pylontech LV-Hub => 70kWh battery storage
1x CerboGX
4x Victron EVCS NS => Auto mode
For example, if a car charges with 11kW on an EVCS and the consumption in the building is 4kW, then the Fronius inverter supplies all loads. When the batteries are full, the Victron MPPTs shut down and only the Fronius works.
If cars are now connected to the other 3 EVCS, they do not start charging, but remain in the "waiting for sun" status.
If I switch one to manual, the Victron MPPTs immediately start up and supply it, then after a few minutes the other EVCS also start in auto mode.
If a cloud appears and the power on the Fronius drops and the existing loads are buffered from the battery, then the Victron MPPTs start up to charge the battery - here too the charging process starts in auto mode, but not otherwise.
In my opinion it is a bug in the system, because the system does not know from the zero feed-in that it actually has a massive surplus, it only has to request it. Actually, the wallboxes should start charging in this situation, then the MPPTs would start up and it is clear that there is surplus. If this is not the case, the charging should simply be aborted and tried again later.
The firmware version of all devices is up to date.
Perhaps you have a tip?
Regards, Marco