question

mfred68 avatar image
mfred68 asked

Mppt rs450/100 spec's

I have lots of roof space and am planning to fit 30 x 415w solar panels (but not all on the same roof) I'm wondering if a 450/100 mppt can handle the following configuration:

Panels are Voc 50v, Isc 10.55A

3 parallel strings of 5 panels in series on one mppt

Making Voc 250V , Isc 31.55A

3 parallel strings of 4 panels in series on the other mppt

Making Voc 200v, Isc 31.55A

Can a 450/100 handle this configuration?

mppt rsmppt calculator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@mfred68

Since you have asked a few solar config related questions, my suggestion to your is use the excel spreadsheet for all your different scenarios.

https://www.victronenergy.com/upload/software/VE-MPPT-Calc-4_0.xlsm

It is important you use the temp coefficient of your panels for I and V.

But off the top of my head if you have one string per tracker you will be fine. No parallel strings on the RS mppts.

FYI you can have uneven strings as well lets you be more flexible for roof set up

VOC is 8 x battery float. See the manual.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mfred68 avatar image mfred68 commented ·

Where do I find the temperature coefficient data?

Here is the label on the back of the panels 1000037750.jpg

0 Likes 0 ·
1000037750.jpg (1.2 MiB)
nickdb avatar image nickdb ♦♦ mfred68 commented ·
Download the panel spec sheet would be the place to start.
0 Likes 0 ·
Show more comments
mfred68 avatar image
mfred68 answered ·

Do you think -10 degrees is a bit over the top, considering the uk rarely gets that cold and if it did, solar production that time of year would be minimal with much lower panel output

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sean avatar image sean commented ·
You are right, but there will be some very cold very bright days (albeit not many in the UK) when the unloaded panel voltage will rise very close to the specified limit, usually early morning in one of my systems - mine simply faults and produces no output untill I reset it, providing ambient has risen slightly the output returns to normal.

Some here will tell you that the world will end if you exceed the controllers max input voltage, but a few volts over the hard limit certainly doesn't harm mine.

0 Likes 0 ·