[UPDATED] Smart BatteryProtect 48V-100A disconnects without error.

Smart BatteryProtect 48V-100A has shut down on four occasions over the last two months. It is controlled via H terminal in Li-ion mode from ATD relay on LYNX Smart BMS. When the shutdown occurs, there is no error on the device or in the app, and ATD is still active. Toggling the Load output switch in the app, or disconnecting and reconnecting the H wire causes it to reconnect. It does not ever reconnect without this manual intervention.


The output of this 48V SBP supplies power to the inputs of two MPPTs which are being used as DCDC converters to charge two other 12VDC battery banks. Is there something wrong with this configuration, or do I have a faulty device?


UPDATE 6/30/24 - I have replaced the SBP under warranty. The new unit has worked well for a couple of weeks then just last night it exhibited the same behavior as the old one and disconnected the loads without error while the app still reported it was connected. Cycling the "on" switch in the app reconnected things.

UPDATE 7/13/23 - The new SBP continues to behave the same way as the old one.


pxl-20240618-094032145.jpg

pxl-20240618-093705582.jpg

pxl-20240618-093808667.jpg

pxl-20240618-093831014.jpg

pxl-20240618-093916333.jpg

pxl-20240618-094258851.jpg

pxl-20240618-094330639.jpg

screenshot-20240618-054415.png

Battery Protectlynx bms
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Phillip Gutowski,

This is not an intended use for the smart battery protect, or the MPPTs.

For switching the MPPTs I would recommend this method instead - https://www.victronenergy.com/cables/ve-direct-non-inverting-remote-on-off-cable

But on top of that it sounds like you're using the MPPTs from a DC supply source other than a solar panel?

That is not supported. We have the Orion range for DC DC charging - https://www.victronenergy.com/dc-dc-converters


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phillip Gutowski avatar image Phillip Gutowski commented ·

Thanks @Guy Stewart (Victron Community Manager),

Would you be able to explain why using a Smart Battery Protect to switch off loads via ATD signal in a lithium battery system is not an approved use?

0 Likes 0 ·
Show more comments
Phillip Gutowski avatar image
Phillip Gutowski answered ·

Any input on this question @Guy Stewart (Victron Community Manager)? Should I RMA the unit a second time?