pearo asked

CoMap InteliLite4 AMF20 Controller issues

I am trying to configure my Cerbo gx to connect to a InteliLite4 AMF20. I have changed all the modbus mapping in the controller to match what the Cerbo requires, and I have even manually tested each modbus register with a modbus tool. I can start and stop the generator using coil 4700 with the modbus tool also.

The Cerbo has detected the Controller, and it shows up in the list of devices. However I keep getting an error "#1 Remote switch control disabled" then it seems to time out as if its disconnected.


The manual says:

If the generator auto start/stop is enabled, it will show error #1 Remote switch control disabled on the Auto start/stop page.

I assume this is the page that is found in settings->generator start/stop? I have the relay set to manual, so no auto stop/start is configured.

I have no idea what's going on. I have looked at comap.py and everything looks ok. I have tried putting the generator in manual and auto modes, I have tested all the modbus registers and they look ok..

Any pointers would be great.


Edit 1:

Just enabled SSH and found this in the logs:

@40000000667166670d8b470c INFO [tcp:10.1.8.134:502:1] Found ComAp InteliLite4-based genset

@40000000667166671435ddc4 INFO registered ourselves on D-Bus as com.victronenergy.genset.comap_intelilite4

@400000006671666c1839a324 INFO [tcp:10.1.8.134:502:1] Device failed: Error reading registers 0x3ec-0x41d: Exception Response(131, 3, SlaveFailure)

Which is odd given I have tested each individual modbus register using ModbusTool

generator auto start
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
nickdb avatar image
nickdb answered ·

Moving to modifications section.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Philipp Trenz avatar image
Philipp Trenz answered ·

Hi @Pearo, Philipp here from the Victron team. Thanks for reporting. I'll reach out to you via email, so that we can take a look at it.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rafal avatar image
rafal answered ·

I have the same issue.

1719048244790.png

1719048256181.png



I sniffed modbus tcp communication and it seems that there is a problem with 4700 coil.
Venus tries to read the 4700 coil:

1719047987628.png


Then InteliLite4 answers:

1719048019316.png


Then Venus tries to write 0000 value to 4700 coil:

1719048071748.png


But again with no success:

1719048095295.png


I read the entire manual for InteliLite4. It seems there is only one condition needed: the genset must be set to Auto (AFAIU), but even though, the problem still persists.

@Philipp Trenz help :)


1719047987628.png (6.9 KiB)
1719048019316.png (8.4 KiB)
1719048071748.png (8.0 KiB)
1719048095295.png (8.7 KiB)
1719048244790.png (24.4 KiB)
1719048256181.png (21.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rafal avatar image
rafal answered ·

OK, I have managed to repair this by upgrading InteliLite to newest firmware :)


1719053130720.png



1719053130720.png (24.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2mas avatar image
2mas answered ·

I have tried updating the firmware

my Cerbo keeps connecting and disconnecting


Some ideas?

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Philipp Trenz avatar image Philipp Trenz ♦ commented ·
Hi @2Mas, we are working on a Venus OS update, that will resolve this issue. Please stay tuned.
1 Like 1 ·
2mas avatar image 2mas Philipp Trenz ♦ commented ·

If you need it testet - just write :-)

0 Likes 0 ·
2mas avatar image 2mas Philipp Trenz ♦ commented ·

@Philipp Trenz Hallo Philipp is the CoMap update included in the new v3,40 version ?

0 Likes 0 ·
Philipp Trenz avatar image Philipp Trenz ♦ 2mas commented ·

Hi @2Mas, unfortunately not. It will be included in the first betas for v3.50, which will soon be available. If it does not cause any issues, we will release a patch version v3.41 soon, which will then include the ComAp patch. Sorry for the delay!

0 Likes 0 ·
2mas avatar image 2mas Philipp Trenz ♦ commented ·

it's okay, there wasn't anything about it in the description of the update either, just wouldn't spend time on it if it's not included ;-)

0 Likes 0 ·
Philipp Trenz avatar image Philipp Trenz ♦ 2mas commented ·

Hi @2Mas, as of now v3.50~5 is available within the Beta update feed, which contains the ComAp readout fix. Please feel free to give it a try and let me know the result.

0 Likes 0 ·
2mas avatar image 2mas Philipp Trenz ♦ commented ·

Hi @Philipp Trenz i´m on it :-)

0 Likes 0 ·
pearo avatar image pearo 2mas commented ·

There is one small issue with v3.50~5 that Philipp is aware of. I just tested the fix and did a remote start of the genset and it worked perfectly.

1 Like 1 ·
2mas avatar image 2mas pearo commented ·

hi @Philipp Trenz and @Pearo , it seems to be steady as a rock, and yes can´t start/stop remote but the connection works now / remains - Good job :-)