question

davidtudor avatar image
davidtudor asked

High Voltage but low amps on solar

Hi, I have 2 RS450/100 MPPT with 4 lots of solar panels around the roof on my house, the solar seems a bit low on one tracker but all the others seem fine, but getting high voltage but low amps, the solar panels are run in series so the amps are low but voltage is high. I have enclosed a screen shot.

1718106830760.png


Solar Panel
1718106830760.png (38.7 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nesswill avatar image nesswill commented ·
Adding to what @Alex Pescaru has said

I usually see this (one or two arrays) drop current but high voltage at the end of bulk start of absorption, what's you SOC?. The system just might not need all of what the arrays can supply.

1 Like 1 ·
davidtudor avatar image davidtudor nesswill commented ·
SOC is 56%
1 Like 1 ·
Show more comments
2 Answers
Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @davidtudor

Switch between each other those two inputs for the XGWVJ MPPT.

If the low voltage is moving to the other tracker, then that string has a problem - some bad connection(s), some bad panel(s), shading, etc.

Or,

There is no need for additional power (more than those 5500W) and that tracker is throttling.

Alex

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

davidtudor avatar image
davidtudor answered ·

Hi Alex, i was watching it and the low amp tracker shot upto 5 amp, but now low again, the other 3 trackers are around the same. screen shot again as the sun is moving.


1718111024782.png


1718111024782.png (29.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.