If your generator is running on auto-start and is manually shut down, will this create a error code (red light). Looks like the fix is to disable and then enable the auto-start again?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
If your generator is running on auto-start and is manually shut down, will this create a error code (red light). Looks like the fix is to disable and then enable the auto-start again?
Yes, you must turn off Auto Start to stop the generator from the GX device. If you stop the generator external to the GX device then the GX device believes the generator is still running. If you connect the generator run to a digital input programmed as Generator then you will get an alert if it is enabled in generator start/stop menu.
GuiMods includes some generator enhancements in this area:
Run time accumulation factors in the state of the Generator digital input: if it's false, then time will not accumulate.
The GX device's manual run state is synchronized by changes in the Generator digital input so that if the generator is shut down externally, the GX device will cancel a manual run. For auto runs, a warning is shown on the Generator Overview page but does not cancel an auto run.
I am having a similar issue. When my generator starts on automatic and I want to discontinue the Run I manually turn it off after placing the auto start in off. When I restore the auto start immediately after the generator has been shut down it restarts. Apparently if the auto start does not see the shutdown parameters it restarts the generator. I have a digital input telling the GX unit that the generator is running.
I made some changes in the autostart logic as part of GuiMods v10.48.
Now, if the start conditions are all satisfied when autostart is enabled, the generator will NOT start.
So now you can turn off autostart to stop the generator manually and it will not restart. Of course it will start if at least one start condition is active.
For example if the SOC start threshold is 30% and the battery HAD reached that level but is now at 50%, turning off autostart, then back on again (after generator is stopped), the generator will remain stopped until the threshold drops below 30% again.
Additional resources still need to be added for this topic
Cerbo GX - Generator auto start/stop
Automatic Generator Start/ Stop [PDF]
Automatic Generator Start/ Stop [Online]
42 People are following this question.