question

Ricardo Chavarria avatar image
Ricardo Chavarria asked

EM530 Issues after installation (Strange Voltage, High Voltage (DC) Alarm, PV Inverter Position)

Hi Everyone.

I've detailed my initial system diagram here. My system now includes an EM530, connected using RS485.

diagram.pngESS set as Grid Metering: Inverter/Charger


I'm noticing three distinct issues.

  1. My PV Inverter won't show if I set it as Position: AC Input 1, Phase: Split Phase (L1+L2) (which is how I've got it setup physically).
  2. Yesterday, I setup ESS to have Grid Metering: External Meter. When the PV Inverter started producing, there was an alarm of high DC Voltage, and the whole system shut down. I had to restart everything. Needless to say, I reverted the settings to have Grid Metering: Inverter/Charger.
  3. The Voltages reported in one of the screens of the EM530 is absurdly wrong: L1-L2: ~160V, L1-N: ~86V.

img-5886.jpegVoltages are incorrect img-5885.jpegVoltages are correct

If anyone can help figure this out, I'd appreciate it. The reason I got a Grid Meter was to have my PV inverter show up in the right spot and to be able to really measure our consumption.


Thanks,

- Ricardo

ESSsplit phasegrid meter
diagram.png (83.7 KiB)
img-5886.jpeg (1.5 MiB)
img-5885.jpeg (1.5 MiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Ricardo Chavarria avatar image
Ricardo Chavarria answered ·
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rickc avatar image
rickc answered ·

Weird voltages: The victron software keeps putting the EM530 into 3phase mode.

You can manually put the EM530 into 2p mode with the buttons, and then recheck the display that looked weird. Every time the cerbo reconnects, it will put it back to 3p mode, however.

As for the High DC voltage, that sounds like a different issue.

Are you sure the CTs are oriented correctly?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Ricardo Chavarria avatar image Ricardo Chavarria commented ·

Weird Voltages: I did notice that my meter was set to 3P...so freaking annoying!! Is there a fix for this? I changed it to 2P, and of course it worked, but it was set back to 3P soon after...can anyone from Victron help here? (@Guy Stewart (Victron Community Manager), @mvader (Victron Energy), @Thierry Cortassa (Victron Energy Staff))?

I tried setting ESS back to Grid Metering: External Meter, and of course as soon as the PV inverter started producing, the same issue happened, the whole system shut down with a High DC Voltage Alarm. I even tried adding a DV Voltage limit in the DVCC menu, to no avail.

My CTs are oriented correctly, just double checked, everything looks good.

About Fronius PV Inverter not being able to be seen when set to Split Phase (L1+L2)...I think this is because it's using solarweb API instead of sunspec API...can anyone confirm?

0 Likes 0 ·
Show more comments