question

toproad1891 avatar image
toproad1891 asked

Orion XS switched from Storage to Off then to Bulk. Why did it switch off?

Float and storage voltage set to 13.3. Re-Bulk offset set to 0.3V Approx 1A continuous load.

The charger had finished charging and had changed to Float, then 8 hours later changed to Storage mode (1 on diagram). The battery voltage gradually reduced and at 13.27V the charger kicked in to maintain the storage voltage.

Then the charger switched off (2 and 3) for 3 minutes and then switched back to Bulk.


Can anyone explain why the charger would have switched from storage to off, and then back to bulk? The battery voltage didn't drop below 13.0 for more than 1 minute which is what I think is needed to cause a re-bulk.




chargerstateandcurrent.png

socandcurrent.png

1715956033311.png

orion xs
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

Because it automatically starts from bulk, then switches through the modes as the criteria to switch are met.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

These detailed plots are much more helpful. From these it looks as if the battery took advantage of increased input power availability

Does your BMS connect to the Cerbo?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

toproad1891 avatar image
toproad1891 answered ·

No, the internal bms is standalone and wouldn't have had any impact here. It only top balances above 14.4V

2 |3000