MP II SOC incorrect and loading with limited power

Hello, I got a Lithium 16 cell battery. I use MP battery monitor at the moment and have standard settings and ESS:

1715880603452.png

1715880629655.png


Problem:

-The SOC is at real 20% from the BMS but here it is:

1715880745013.png

-Means it drops until low voltage alert with 47V but still has 85% SOC. What configuration did I do wrong?

- Whatever I do, i can load only with 500W max, although I do not limit charge power. What is wrong here?

1715880909033.png


Thank you

Multiplus-II
1715880603452.png (6.6 KiB)
1715880629655.png (7.0 KiB)
1715880745013.png (7.6 KiB)
1715880909033.png (20.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

@stern You will need to tweak these 3 settings.

batt-mon.png


batt-mon.png (86.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stern avatar image
stern answered ·


my settings are:

1715957715304.png


changing this seems to me improving long time measurement. I am missing a ways to tell the MP

-now, that the battery is in undervoltage condition, please assume <5% SOC instead of 90%



1715957715304.png (36.5 KiB)