...according to changelog of Venus OS v3.30-10 and this https://www.victronenergy.com/live/drafts:dynamic_ess#qwhy_does_the_system_exceed_the_configured_power ...the settings should show up in my GX.
I have an EM540 as grid meter, GX is running v3.31 and a 3ph-MP2 setup is running v510 and ESS assistant 018C.
So what's the deal here?
@Dirk-Jan Faber (Victron Energy) ...there is a new law introduced in germany, for all grid connected battery systems, that are capable of drawing above 4.2kW from the grid. The system needs to be enabled to be externally triggered by the DSO to reduce input power to 4.2kW.
See here: https://www.bundesnetzagentur.de/DE/Fachthemen/ElektrizitaetundGas/Aktuelles_enwg/14a/start.html
This is true for all new installations starting from Jan 1st 2024.
The Operator/Owner is required to enable the external control by the DSO
Luckily the DSO currently has no means of sending the trigger (yet), but will be soon as smart meter rollout will increase.
Most likely it will be implemented by a control box and a NO/NC potential free switch/relay...but for some installations another method, probably via IEC61850 and scheduled charging could be chosen, too.
Something to take into account for (D)ESS systems in Germany....