"Temperature Alarm" Quattro 48/10000

New equipment installed 2 x Quattro 48/10000

Firmware updated to V510

When the installation starts, the Master with around 2000W of load, the Temperature led start and turns off.

After a few moments, the inverter restarts normally.


Any suggestions to try to solve this problem?

Thanks


MultiPlus Quattro Inverter ChargerTemperature Alarm
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·
have you tried one unit at a time.

I presume you have set them up in parallel so try them one at a time and see if the same issue occurs but only in one unit.


0 Likes 0 ·
Diogo Baptista avatar image Diogo Baptista Paul B commented ·
The system is in pararel. We tested each unit individually and only one is giving the temperature error.
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Diogo Baptista commented ·

@Diogo Baptista

If you are comfortable, open it and check that all the connectors are fully seated. If there is nothing obviously loose or it does not solve the issue. ....Return it for an RMA.

0 Likes 0 ·
1 Answer
Diogo Baptista avatar image
Diogo Baptista answered ·
I already do this and check all the connectors.


I will do a RMA to this equipment!


Thank you for your help.