question

Diogo Baptista avatar image
Diogo Baptista asked

"Temperature Alarm" Quattro 48/10000

New equipment installed 2 x Quattro 48/10000

Firmware updated to V510

When the installation starts, the Master with around 2000W of load, the Temperature led start and turns off.

After a few moments, the inverter restarts normally.


Any suggestions to try to solve this problem?

Thanks


MultiPlus Quattro Inverter ChargerTemperature Alarm
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·
have you tried one unit at a time.

I presume you have set them up in parallel so try them one at a time and see if the same issue occurs but only in one unit.


0 Likes 0 ·
Diogo Baptista avatar image Diogo Baptista Paul B commented ·
The system is in pararel. We tested each unit individually and only one is giving the temperature error.
0 Likes 0 ·
Show more comments
1 Answer
Diogo Baptista avatar image
Diogo Baptista answered ·
I already do this and check all the connectors.


I will do a RMA to this equipment!


Thank you for your help.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.