question

doppeldecker1678 avatar image
doppeldecker1678 asked

Problems with RS485 adapter to connect with ET340

Hi all,


I am new to this and setting up the first ESS with a Multigrid 48/3000 on Venus GX and ET340.


Unfortunately I do not get to run communication between ET340 and Venus GX via the Victron USB to RS485 adapter.

I did connect as said Data +, data - and GND between ET340 and the RS485 adapter. The left led on ET340 stays green instead of blinking red as I would expect if communication was enabled.

On the Venus GX no energymeter is available.

No difference wheter or not I use a terminator or not.

Does there need to be sth. enabled in the Venus GX? I did enable ModbusTCP, is that relevant by the way?

Hope somebody can give advice how to search for the solution step by step.


Best regards

Sascha


Venus GX - VGXEnergy Meterrs485
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
doppeldecker1678 avatar image
doppeldecker1678 answered ·

First of all, thank you all for your immidiate support.

Secondly: SORRY! I simply failed to squeeze the wire end sleeves clean. This way a data channel simply had no electrical contact.

After correction, everything workes fine. Special thanks to Peter at this point.

Without any cable extension NO termination is enough. After having added 7m of cable, I used the internal termination of ET340. System working stable.


Best regards,


Sascha

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Peter Polz avatar image
Peter Polz answered ·

Hi Sasha

Because of talking each other that morning over an other Forum here my already given answer to complete that request. Connecting with a longer cable normale requires the termination of Modbus with 120 Ohm. The venus attached Rj45 "Canbus" Terminator is "not" the correct Terminator for the Rj45 connection on the ET340. For termination direktly on the ET you can bridge the internal restistor with a bridge between A- to T directly on the ET340

@mvader (Victron Energy Staff) may you can add a generell info concerning termination of Modbus with extended cables to https://www.victronenergy.com/live/energy-meters:et340 because thats an often asked question of installers

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image wkirby ♦♦ commented ·

Also, to add to what Peter said about termination. There is a 120 Ohm terminator on the green and brown wires of the Victron USB adapter. You need to use that terminator there also.

You did not mention here that you were using a longer cable, that would have been useful information for us. You really need the terminators for long cable lengths.

0 Likes 0 ·
Peter Polz avatar image Peter Polz wkirby ♦♦ commented ·

Really there is also an integrated on the green and brown ?. Damn good to know!!!.. i always added an extra 120Ohm to Adapter A/B. That should really be mentioned in manual. Because on "live" page there was written "The red, green and brown wire coming out of the USB to RS485 cable are not used. "

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ Peter Polz commented ·

I got that information from the OEM datasheet:

https://www.ftdichip.com/Support/Documents/DataSheets/Cables/DS_USB_RS485_CABLES.pdf

Maybe the information should be included in Victron manuals. Also there is no mention of the terminators present in the Carlo Gavazzi meters.

0 Likes 0 ·
Peter Polz avatar image Peter Polz wkirby ♦♦ commented ·

In offical manual attached to ET340 BOX, the internal terminator on A- T is mentioned but most of User don't take care of that mini manual and just look on the online live page. See "Connection digrams Fig. 8"

0 Likes 0 ·
Izak (Victron Energy Staff) avatar image
Izak (Victron Energy Staff) answered ·

Let me first address the claims regarding termination.

The rule of thumb is: If the propagation delay of the data line is much less than one bit (pulse) width, termination is not needed.

On a 100 meter cable (round trip of 200m), assuming 300 000 km/sec speed of light and propagation time of around 67% (so 200 000km/sec), propagation delay on the line is 1µs. The pulse with at 9600 baud (which is what is used in this application) is 100µs. So termination should not be required for any of the cables Victron sells. Also see here.

Also, as @WKirby points out, it is already terminated on the one end.

Inside the USB plug there are two LEDs, a red one and a green one. Whenever there is outgoing data (a request to read a register) the red LED will flash, and when there is a response the green one will flash. This can help you to figure out what is going on. You should see the two LEDs flash alternately. If you only see the red one flashing and no green (or intermittent green), then there is a break or disturbance in the communication somewhere. I would start here, and if comms appear to be fine on this level, then have someone from tech support look on the Venus device if the device is detected and working properly.


I've had quite a few cases in the past where the device is in fact detected but the connection is so poor that 90% of the data fails a CRC test and it never manages to complete acquisition of the meter.
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

raymiller avatar image
raymiller answered ·

I had some issues connecting my Venus GX to the ET340 Carlo Gavazzi energy meter using a USB-RS485 adaptor with a non-FTDI chipset.

While I was able to connect the ET340's to my Windows 10 computer using the non-FTDI chipset and operate the Carlo Gavazzi configuration software, and set the second ET340 energy meter to address "2", when I then connected to the Venus GX nothing would communicate. It was only when I managed to purchase a Victron USB-RS485 which uses the FTDI chipset did everything work. To get the windows 10 computer and the Carlo Gavazzi configuration software to talk to each other I also needed to get a driver for the Victron Energy USB-RS485 converter (you need an internet connection).

The ET340 manual (extract 4. below) states you will need two USB-RS485 adaptors to connect more than one ET340. This is not the case if you use the Carlo Gavazzi software to change the default address 1 to 2 and then connect the second ET340 energy meter to the same RS485 bus. This saves the added cost of the RS485 adaptor and frees up the second (or remaining USB port). The added advantage of connecting your Windows 10 PC is that the correct operation of the energy meters can be check before connecting the RS485 bus to the Victron Venus GX or similar.


"4. Multiple Energy Meters in one system

To connect multiple Energy Meters, wire each meter to a separate RS485-USB converter. Which are then each plugged into a separate USB socket on the CCGX.

Connecting multiple ET340 meters to the same RS485-USB cable is not possible: the ET340 meter has no display and its Modbus address can therefor not be changed."


Re RS485 line terminations, while in theory, a 120ohm termination should do no harm on the RS484 bus even for a short cable length, I experienced communications issues with the USB RS485 adaptor when the cable was terminated. When all terminations were removed everything worked well. This termination issue only seemed to apply to my non-FTDI chipset adaptor.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andreas-ott avatar image
andreas-ott answered ·

Hello

I had problems with connections too. I removed the Termination and everything goes fine.

Andreas

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic