I would like to use "Time of day" as a conditional in structuring VEConfigure assistants.
Is this a possibility?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I would like to use "Time of day" as a conditional in structuring VEConfigure assistants.
Is this a possibility?
The inverter has no internal clock.
Using the generator input from the GX to set timers and signal and internal relay with the GX relay for time based things. I use it to trigger an AC2 out at certain times.
Also had it once to connect to grid at certain times to treat it like a generator.
More sophisticated way is to use node red integrations on Venus is large.
Have wondered this in the past. Does it work on the MPII-GX variants which AFAIK do not have a GX relay output?
No idea, don't use them for anything more than a simple ESS or back up solution.
But node red is an option here and it has time built in.