Hello
The more i investigate the more confused I get. My system:
4 ea 200Ah Smart LiFePo4 Victron batteries in parallel (12v)
1 ea Lynx Smart 500 BMS
1 ea MP2 120v/3000W
1 ea Cerbo with Display
1 ea SBP 220a
2 ea MPPT 100/30 controllers
I have my my BMS SoC threshold set to 70%. My MP2 charge parameters set to Battery type --LiFepo4 w/Lithium batteries/ Batteries icon box checked /Absor Voltage to 14.2/Float Voltage set to 13.5. Cerbo DVCC is Forced on with all parameters as in default settings. Side note: I have also enabled the VE Smart Networking on the MPPT's and the MP2.
My SOC now on my battery bank is 62% yet the MP2 charger never activated. My understanding was that when the MP2 was "told" via the bus system that my SOC fell below 70 % then I should start charging. What am I missing?