Hello, I have the Multi RS Solar Dual MPPT (6000 W total - 3000 W per tracker).
1- In the manual and specs it says that the "max Voltage of the device is 450V".
Is this the max Voltage for each array (this device has two MPPTs) or is it the sum of both arrays ?
So lets say I have two arrays, each array is by 6 Panels with VOC 46V, so each array has VOC 276V. If the max Voltage is per array, then I can connect the 12 panels in total, putting 6 for each array. If the max Voltage is ment for the "device" as they say in the manual, then I cannot connect the 12 panels as described above.
2- Similar question would be for the Start-up voltage: 120 V - per array or the voltage of both arrays together ?
Please help in these two very important questions. Thanks.