question

m66b avatar image
m66b asked

Enphase PV system doesn't deliver power when offgrid

System: Multiplus II GX 5000/70 + Pylontech US5000

Software: v3.30~13, ESS assistant configured (see screenshots below)

Connections: grid on AC IN1, consumers and Enphase system on AC OUT1

Grid: the Netherlands (EN50549-1:2019), configured in both Enphase/Victron

As soon as the grid is disconnected, the Enphase system stops delivering power. It tries to send a bit of power (50-100 Watt, see the graph below), but it turns off each time.

The graph starts and ends with grid power on. The test was deliberately with only some solar power (~300 Watt), but with more solar power, the same problem occurs.

The Enphase system is fed with 230 Volt and 50 Hz by the Victron (measured with an SDM120 energy meter), so everything is seemingly fine.

It was suggested to change the grid profile of the Enphase system to one of the GB profiles because it was said to tolerate a less perfect sine wave, but that didn't help to solve the problem.

I've checked the settings already many times, but so far, I haven't found a solution. So, any suggestions are welcome.


screenshot-from-2024-03-12-09-52-24.png

screenshot-from-2024-03-12-11-17-59.png

screenshot-from-2024-03-12-11-16-01.png

screenshot-from-2024-03-12-11-16-13.png

screenshot-from-2024-03-12-11-16-24.png

screenshot-from-2024-03-12-11-16-31.png


Multiplus-IIenphase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

9 Answers
nickdb avatar image
nickdb answered ·

Have you tried with production GX code and not the beta?

I would eliminate that as contributing.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image m66b commented ·
I switched to the beta hoping this problem would be solved.
0 Likes 0 ·
Michelle Konzack avatar image
Michelle Konzack answered ·

Are you sure, you want to restart the PV charging if the DC Voltage goes under 40V?

Looks VERY LOW

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image m66b commented ·

That's in the case of overvoltage only, as far as I understand, but I'll try other values anyway. Thanks for the suggestion.

0 Likes 0 ·
m66b avatar image m66b m66b commented ·
I've tried 51 volt, but it doesn't resolve the problem, unfortunately.
0 Likes 0 ·
juergenal avatar image
juergenal answered ·

You have the wrong Setup parameters in the frequencies shifting. I have at the moment nothing for netherland but look at the other table setup for other countries and change you frequencies.

enphase1.pngenphase2.png


enphase1.png (126.0 KiB)
enphase2.png (133.5 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image m66b commented ·

The frequencies are correct for the Netherlands, and in fact, I tried to change the frequencies already (not all combinations).

The frequency fed to Enphase is 50 Hz, though.

0 Likes 0 ·
Duivert NL avatar image
Duivert NL answered ·

hi, im in the netherlands to, no experience with enphase but growatt


i think your using the wrong gridcode, should be:

schermafbeelding-2024-03-12-134615.jpg

see also:https://community.victronenergy.com/questions/34659/ess-not-possible-in-the-netherlands-at-least-not-w.html


not related but also 1 us5000 on a multiplus 5000 is to small, you need at least 2


5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image m66b commented ·

The correct grid code for the Netherlands is EN50549-1. It wouldn't be compliant to use something else, but I can try, of course.

About the battery: this is a small system to start with. It will probably be extended if everything works as expected.

0 Likes 0 ·
Duivert NL avatar image Duivert NL m66b commented ·
Hi, yes you are indeed right about the grid code!


been a while since i set my 3phase system up, german gridcode was the advice to use back then
0 Likes 0 ·
Show more comments
ton-gans avatar image
ton-gans answered ·

Hoi, I'm in the Netherlands and have Enphase on AC-out. The frquencies I use are: 50.20, 50.80 and 51.50 Hz. Grid code Europa. See attached documentEnphase Energy - Enlighten _ EN 50549-1_2019 RfG E02 Netherlands gridprofiel.pdf


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image m66b commented ·
I'm certainly going to try this, thanks, but when will there be sun again? ;-)
0 Likes 0 ·
m66b avatar image m66b m66b commented ·
I've changed the frequencies as suggested, but it doesn't help unfortunately.


I would appreciate it if you contacted me via marcel<at>bokhorst<punt>eu and sent me your VEConfigure file, so I can compare settings.

0 Likes 0 ·
m66b avatar image
m66b answered ·

Also tried without success:

  • Disabled Loss-Of-Main detection via VEConfigure
  • Switched to no export grid profile via Enphase Enlighten
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Duivert NL avatar image
Duivert NL answered ·

hi maybe this document can help a bit? (its in dutch)

https://enphase.com/nl-nl/download/ac-koppeling-enphase-iq-microinverters-met-victron-accu-omvormers-voor-residentiele

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

m66b avatar image
m66b answered ·

Miraculously, it started working, with the same setup, although a ferrite ring was added. Perhaps due to a firmware update of the microinverters?

Maybe this is useful to somebody else:

Enphase:

  • Non metered gateway (firmware: D7.6.358)
  • 8x IQ8PLUS-72-M-INT
  • Grid Profile: EN 50549-1:2019 RfG E02 Netherlands
  • Firmware version: 521-00005-r06-v08.05.02

Victron:

  • 1x MultiPlus-II GX 48/5000/70-50 230V
  • Grid Profile: Europe EN50549-1:2019 + LOM B
  • ESS frequencies: 50.20, 50.80, 51.50 (works too with 50.20, 51.20, 51.50)
  • Firmware version: v3.40~2


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Duivert NL avatar image Duivert NL commented ·
Good to hear its working now! Hopefully no other issue’s because V3.40~2 is still a beta
0 Likes 0 ·
mfred68 avatar image
mfred68 answered ·

Can you please explain what you did to get it working? I'm having the same problem, I'm in the uk.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources