Dear all,
i tried many things but at this point i would like to ask for help.
I have a 3 phase system of Multiplus2 3000VA that work per individual phase not in group. So each phase compensates itself via EM24 to zero Watt going out side. The PV Inverters are all AC coupled. So my MP2 work as intelligent Charger taking any power per phase that would go out of my house.
I set VDCC as follows:
In addition the MP2s are limited to the max of 32A, but i HOPE this means each of them is limited to 32Amps.
Else i could not find any place in VenusOS to set any limit. In Pylontech Menu i see the 150A limit as a parameter that anyhow cannot be changed.
My PV is rather small with 2500Wp, and varies per phase....
So like now i have 1200W on L2|| and 800W on L3|| and 200W on L1|| coming from PV.
On EM24 i see a Power of 400W going out of my house......on L2 i see a charging of arround 800W going to the Pylontechs, and on L3 i see also 800W going into Pylontechs...so overall its DC 50V / 30A......
Which of course is not as planned. I would have expected the 50A to be possible, so WHY does the L2 inverter not take all the 1200W??? going into my battery.
Is anyone here who can tell me PLEASE what i could have set wrong? or forgot to set at all.
Thanks a lot,
Norbert