Is it possible to work with a 1-phase network connection to a three-phase Multiplus II own network with ESS, which then only works on phase 1 (L1)?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is it possible to work with a 1-phase network connection to a three-phase Multiplus II own network with ESS, which then only works on phase 1 (L1)?
To have a single phase input on a three phase system, it requires switched as a group to be off. So if you have three phase AC PV ESS will not work.
With the other two phases not having grid all the features of ESS fall away anyway on those two phases.
Thanks for the explanation, when setting up the ESS assistant was also turned off automatically. I thought maybe it had to do with the Gridcode settings.
Additional resources still need to be added for this topic
41 People are following this question.