VE Direct Hex Protocol Alarms (SmartShunt)

Hello,

is it possible to get the alarm states with Hex Protocol? In the documentation I only found how to change the alarm settings.


Thanks a lot

SmartShuntVE.Direct
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Michelle Konzack avatar image
Michelle Konzack answered ·

The HEX protocol is only used for configuration.

If you want to get the STATUS from a VE.Direct device,

you have to use the TEXT protocol which is endless streaming.

You have only to capture it.